Posted on Sunday, October 1, 2017 on product Sloan ETF-450-A Control Module Assembly (for ETF or EBF Series Faucets)
-
0voteA:
If the Faucet does not deliver any water, you can test to see which part is defective by disconnecting the power and then reconnecting the power.
A) If the Green Light illuminates when power is reconnected, replace the Sensor.
B) If the Green Light does not illuminate when the power is reconnected, replace this ETF-450-A Splash Proof Junction Box (Part #101474).
If you have any other questions our experts are here to help! Call or text 800-518-5388
Posted by Kully Supply on Tuesday, October 3, 2017
Posted on Monday, September 19, 2016 on product Sloan ETF-450-A Control Module Assembly (for ETF or EBF Series Faucets)
-
0voteA: There is not a spec sheet specific to this part. This part goes into a handful of different Sloan faucet models. Below is a link to the PDF troubleshooting guide and parts breakdown for some of those faucets. www.sloanplumbingparts.com/pdf/sloan/14-%20ETF%2080,500,%20600,%20610,660,770,%20700.pdfPosted by Kully Supply on Monday, September 19, 2016